Hey,
I am going to install 2 PS Audio Power Port duplex receptacles for the hi fi system of a buddy audiophile of mine this weekend, and I have some questions regarding the fact that these duplexes have an isolated ground. He has two 15A 14/2 romex dedicated lines. Each line will have a single duplex, and that's it. I know the Power Ports are 20A and that by code it's illegal to wire a 20A duplex on a 15A line but my friend does not have power hungry components and he will be only using 15A anyway so this should be fine. His house was built in 2012 so electrical is fairly recent. So, about the isolated ground, how to I wire this with a 14/2 wire? Do I do like any other duplex where I wire the black wire on the brass screw, the white wire on the silver screw and the bare copper ground wire on the ground screw? I have read online that a third red wire would be used with those duplexes. I am a bit perplexed on this. I understand that the two ground pins are connected to the ground screw and that the ground screw is isolated from the yolk. So if I wire like I do normally with standard duplexes, it should not be an issue.. unless I missed something? :scratch2: Thanks for your input |
Why would it be "illegal" to install a 20 amp rated outlet on a 15 amp circuit as the outlet will only draw whatever current the breaker rating allows for and no more. Wire the outlet the same as the one you replace it with. You're only replacing a cheap builder spec outlet with a better built one.
|
Is that 14/2 with no ground conductor, or does it have a ground?
|
Isolated Ground on Duplex Receptacle
See NFPA NEC 210.21(B)(3) Receptacle Ratings. The NEC speaks to this via a table in the section I referenced above.
You cannot use a 20A outlet on a branch circuit rated for 15A because the 20 A outlet allows equipment drawing more than 15A to be connected the branch circuit. A 15A outlet limits the current to 12A as that is the maximum current that an appliance having a 15A plug can draw. As a practical matter in your friend’s case it doesn’t make any difference since he is connecting low current equipment via the 20A outlet. |
Quote:
|
Quote:
|
Isolated Ground on Duplex Receptacle
1 Attachment(s)
Quote:
:thumbsup: The 20A outlet has the horizontal slot allowing a plug meant for both a typical 15A or higher 20A load whereas the 15A outlet only allows a plug meant for a max of 15A. Attachment 62946 |
Only 1 issue out there that I am surprised noone has flagged namely that the majority of powercords that are supplied or available on order which are 20amp, have 20amp female at the component end but for some reason are shipped with 15amp male plugs, not the proper 20amp male with one vertical and 1 horizontal blade.
|
Isolated Ground on Duplex Receptacle
Quote:
Interesting. I’ve not seen that. They simply shouldn’t exist and I know CSA and UL would have serious heartburn over that. |
Quote:
All that stated, the best move is to ensure you order the right male termination. |